How many receptacle outlets are permitted on a 20A, 120V circuit in a commercial building?

Study for the New York City DOB Master Electrician Exam. Use flashcards and multiple choice questions with hints and explanations. Boost your exam readiness!

Multiple Choice

How many receptacle outlets are permitted on a 20A, 120V circuit in a commercial building?

Explanation:
In a commercial building, when determining the number of receptacle outlets that can be connected to a 20A, 120V circuit, the National Electrical Code (NEC) provides guidelines indicating that each receptacle is calculated based on the maximum load it can handle. According to NEC Article 210.21, for general-purpose branch circuits, each receptacle outlet is generally considered to draw a maximum load of 180 VA (volt-amperes). The total capacity of a 20A circuit at 120V is: 20A x 120V = 2400 VA. To find out how many receptacles can be installed, you divide the total circuit capacity by the load per receptacle: 2400 VA / 180 VA per receptacle = approximately 13.33. Since only whole outlets can be installed, this leads to a maximum of 13 receptacle outlets on a 20A circuit. Therefore, option B is the correct answer, as it accurately reflects the maximum number of receptacles that can be installed while adhering to NEC guidelines for a 20A, 120V circuit in a commercial setting.

In a commercial building, when determining the number of receptacle outlets that can be connected to a 20A, 120V circuit, the National Electrical Code (NEC) provides guidelines indicating that each receptacle is calculated based on the maximum load it can handle. According to NEC Article 210.21, for general-purpose branch circuits, each receptacle outlet is generally considered to draw a maximum load of 180 VA (volt-amperes).

The total capacity of a 20A circuit at 120V is:

20A x 120V = 2400 VA.

To find out how many receptacles can be installed, you divide the total circuit capacity by the load per receptacle:

2400 VA / 180 VA per receptacle = approximately 13.33.

Since only whole outlets can be installed, this leads to a maximum of 13 receptacle outlets on a 20A circuit.

Therefore, option B is the correct answer, as it accurately reflects the maximum number of receptacles that can be installed while adhering to NEC guidelines for a 20A, 120V circuit in a commercial setting.